Listed GEC /Rod Clamp?

Status
Not open for further replies.

websparky

Senior Member
Location
Cleveland, Ohio
This is the first one I have come across.....is it listed for a rod electrode??

gecpipe.jpg
 
Re: Listed GEC /Rod Clamp?

It looks like an old pipe electrode which does not need a listing. The clamp and GEC on the other hand . . .
 
Re: Listed GEC /Rod Clamp?

that clamp was the typical clamp 15 to 25 years ago. do not have a NEC that old but that was what looked common in CA back then. stranded was allowed and the rod looks driven to me (in soft soil). paul
 
Re: Listed GEC /Rod Clamp?

Greaves makes a listed DB clamp that looks just like a water pipe clamp - it is stamped with a DB on it. The one shown does not look like it is listed for the purpose.

Pierre
 
Re: Listed GEC /Rod Clamp?

Can't really tell by the pic, but all the DB clamps I have seen use brass or stainless screws.
 
Re: Listed GEC /Rod Clamp?

Anybody note the seperate rod for the telco/cable? one violation. :D LOL

The clamp shown can be used for ether pipe or rod by reversing the back side of the clamp. if you look close you will see that the clamp bottomed out before it was tight, possably why the installer bent the screws over. reversing the back side of the clamp will give it a range all the way down to a 1/4" rod (like the ones the telco use to use) And Dean is correct listed clamps for DB or rain exposed areas will have brass or stainless steel screws and hardware not the steel screws you find on most ground straps for indoors that don't even have to be listed.
 
Re: Listed GEC /Rod Clamp?

The clamp looks like a pipe/tubeing connector... not rated for ground rods. What about the electrode being driven flush/below grade? The connector should be rated for direct burial. The conductor should be secured to the surface it is run on. The electrodes should be connected together.
Rick
 
Re: Listed GEC /Rod Clamp?

A point to consider here is that any approved listing is nullified and doesn't mean a thing if it is installed incorrectly.
For example: You may want to rate your conductor ampacity for 90 degree Celsius. When the system fails because 75 degree Celsius terminals were used... Then, terminals that are 90 degree Celsius rated but torqued incorrectly are useless; the testing laboratory isn't accountable, the manufacturer is not in any way accountable. Too many ugly things goin' on in my trade fellas.
grandpapastu.

[ June 04, 2004, 02:30 PM: Message edited by: grandpapastu ]
 