What you were told is actually a twist on the matter, which has nothing to do with the listing. The actual violation is that the stripped conductors in a raceway are not an NEC recognized wiring method. Conductors run in raceway must be of a type in Table 310.104(A).
Does this tie cables to 310.104 & the previous UL section does use 600V in its rating of non metallic cable
310.10 Uses Permitted
The conductors described in 310.104 shall be permitted for use in any of the wiring methods covered in Chapter 3 and as specified in their respective tables or as permitted elsewhere in this Code.
(A) Dry Locations. Insulated conductors and cables used in dry locations shall be any of the types identified in this Code.