wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
No. That computation would only apply if you disconnected the neutral-ground bond at the service, shorted the line conductor to your GES, and measured the resulting line-neutral voltage at 118.3 (since the neutral is still connected to the utility GES) and the current at 1.7A.118.3 volts / 1.7 amps = 69.6 ohms for GES ?
Did you measure the current on the GES with no load? Is your current measurement accurate in the 1-2A range? Are you on city water with a metallic water service? Because with a current division of 1.7A / 32.8A, the GES resistance seems very low, as per my earlier computation.
Cheers, Wayne