petersonra
- Northern illinois
- Semi-retired engineer
You are misunderstanding how this stuff works.Hi Bob,
out of the Siemens Handbook for UL "http://www.automation.siemens.com/tip-static/dlc/en/Low-Voltage-Distribution-Boards/The_Secrets_of_UL_and_NFPA.pdf"
Which standard applies?
Before configuration, it is necessary to clarify which standard is applied in which application cases. When to use UL 508A? When to use NFPA 79? When to use both?
The requirements and interfaces of both standards are clearly set out with regard to most points. If requirements overlap, however, the standard with the higher
requirements in relation to the respective point must be applied.
I was thinking, if something is not regulated in UL508A I have to look into NFPA79....
Not correct?
Andreas
In much of the US, the electrical codes do not require control panels meet either UL508a or NFPA79. They are both voluntary.
In some of the US, localities have added a requirement that control panels be listed. The only listing standard available for control panels is UL508a. One can also make a very good argument that OSHA requires control panels be listed although this requirement is widely ignored.
NFPA79 also covers other parts of the electrical design of machines that are not included in UL508a. However, it is a completely voluntary standard. Having said that, you have to design to some standard or you will incur liability in the court system. You can make up your own and defend it yourself, or you can use a widely recognized standard like NFPA79. It is just a lot easier and more cost effective to use NFPA79 over something else.
My understanding is that UL508a includes all the requirements for control panels that are also found in NFPA79. So, if one uses a UL508a listed control panel on an industrial machine, the control panel part already meets NFPA79. NFPA79 has additional requirements for things outside of the control panel, so using a UL508a control panel does not mean that the whole machine meets the requirements of NFPA79.