Load calc in VA when only given MCA?

liam913

Member
Location
Boston
Occupation
Electrical Engineer
I know the MCA is only provided for wire sizing. I need to get load calcs for different mechanical HVAC items. Some items give me both FLA and MCA and then some just give me MCA.

What do I do if only given MCA??
 
MCA (Minimum Circuit Ampacity) is a value used to determine the minimum wire size needed to safely carry current for a motor or electrical system, while FLA (Full Load Amps) is the rated current a motor draws at its full load operating condition. MCA is typically 125% of the FLA.
With FLA, you can then calculate VA
 
The way I read 220.50(B) you need to use the MCA in your load calcs.
(B) Air-Conditioning Equipment.
The conductor sizing requirements specified in Part IV of Article 440 shall be used to determine air-conditioning loads for hermetic refrigerant motor-compressors.
The conductor size is based on the MCA
 