load calc on 12kw range

Status
Not open for further replies.

QES

Senior Member
Location
California
can anyone help me explain me how to calc. load on a range of 12kw table 220.55 on range over 8.75 kw is unclear for me.
 
Jimmy, a single 12 KW range has a demand of 8 KW per column C.

I know your probably looking for something more.

Roger
 
I was looking at the wrong way, so for any range 8.75-12kw it will be just 8kw. I was doing it the hardway.

so for 15kw range:
at 5% increase for every 1 kw over 12kw = 9.2kw correct?
 
Jimmy, sorry it took so long for me to get back to you, for a 15 KW range 9.2 is correct.

Roger
 