Would this be correct or right for calcs on a single family with a steam unit in the shower?
Non-Motor Loads
3VA per ft? 3119ft? 9357VA
Appliance circuits 2ea 3000VA
Laundry 1500VA
Refrigerator 1344VA
Dish Washer 1080VA
Dryer 4500VA
Steam Unit for Shower 15000 VA
Water Heater gas 0VA
Microwave 1000VA
Range/Oven 8000VA
TOTAL 44781VA
1st 10kVA 10000VA
Remainder (34781VA) @ 40% 13912.4VA
Motor Loads
1st Air Conditioner 125% 40A/240V 9600VA 12000VA
2nd Air Conditioner 100% 24A/240V 5760VA 5760VA
1st Furnace 125% 12A /20V 1440VA 1800VA
2nd Furnace 100% 12A/120V 1440VA 1440VA
Pool Motor 100% 12.5A/240V 2400VA 2400VA
47312.4 VA
?240 V
197A