After reading some of the recent posts I realized I don't full understand a few things about smaller services. What I'm not clear on is taps at the meter and sizing breakers.
Lets take a detached shop and a small house. Load calc on shop is 60amps. Calc on house is 100amps. Going to put in a 200 amp service. Going to meter at shop. Going to put a 100 amp panel in shop. Also will be putting in a 200 amp panel in the house. Both will be tapped in the meter can.
Load calc says 160 amps but potential draw is 300. If it was a overhead mast and you sized your conductors for 200amps you could pull 300 on them in the future if load was added. I'm just a little confused as to if that is legal and if 230 covers this in a way I'll be able to understand. Some code references or online docs would be helpful to get me pointed in the right direction. Thanks!
Lets take a detached shop and a small house. Load calc on shop is 60amps. Calc on house is 100amps. Going to put in a 200 amp service. Going to meter at shop. Going to put a 100 amp panel in shop. Also will be putting in a 200 amp panel in the house. Both will be tapped in the meter can.
Load calc says 160 amps but potential draw is 300. If it was a overhead mast and you sized your conductors for 200amps you could pull 300 on them in the future if load was added. I'm just a little confused as to if that is legal and if 230 covers this in a way I'll be able to understand. Some code references or online docs would be helpful to get me pointed in the right direction. Thanks!