Ah, the service OCPD is also the feeder OCPD, so 215 applies to that also. Thanks, basic oversight on my part.
Thus in my subsequent post, the Service OCPD would have to be 225A per 215.3. Which means the Overhead Service Conductors would have to be 225A as well, and everything on the service has to be 225A.
So the allowance on sizing the Overhead/Underground Service Conductors at 100% of the calculated load is only useful when there are two or more service disconnects. E.g. say you have a service with two disconnects supplying two different feeders, each with a load of 40A continuous, 60A non-continuous. Each service OCPD and set of service entrance conductors would have to be rated at 110A. But the Overhead/Underground Service Conductors (if any) would only need to be 100A.
Thanks, Wayne