electricalintern
Member
- Location
- PA
- Occupation
- Intern in Highschool
If there are a total of 30 Cooler Fridge requiring 120V/12AMP each, can I use a Table 220.44 (Demand Factor for Non Dwelling Receptacles Loads) to reduce the total load
This place is consider to be a beer distributor warehouse, so I don't think I can use Table 220.56 (Demand Factor for Kitchen Equipment - Other Than Dwelling Unit).
How can I lower the total load for each Cooler, or do I need to use 100% of the load since it's consider to be a refrigeration equipment.
Same question if I have a Walk in Box, do I need to use 100% of the load when creating a Panel Schedule?
When calculating the load for a Rooftop Unit, do I always used 100% load of the FLA?
What happens if I only have the MCA from the cutsheet?
I looked at section 440.33 (Motor Compressors(s) with or without additional Motor Loads) but was a little confused on how to calculate the Walkin Boxes and Rooftops Units loads.
This place is consider to be a beer distributor warehouse, so I don't think I can use Table 220.56 (Demand Factor for Kitchen Equipment - Other Than Dwelling Unit).
How can I lower the total load for each Cooler, or do I need to use 100% of the load since it's consider to be a refrigeration equipment.
Same question if I have a Walk in Box, do I need to use 100% of the load when creating a Panel Schedule?
When calculating the load for a Rooftop Unit, do I always used 100% load of the FLA?
What happens if I only have the MCA from the cutsheet?
I looked at section 440.33 (Motor Compressors(s) with or without additional Motor Loads) but was a little confused on how to calculate the Walkin Boxes and Rooftops Units loads.