So I am trying to figure the optional calculation for a service feeding a laundryroom in a
apartment complex. this service has no other loads.
trying to figure how much load can be added to this existing service, We will be adding a subpanel later
for some Electric Vehicle charging.
I used the nameplate ratings on the equipment : Art. 220.82 (b)
service is 200a 120/240 1ph.
1.water heater 80 gal x 1 5616 watts 5616
2. washer machine x 6 7.0a ea. x 120v 5040
3 dryers x 6 5900 watts ea. 35400
4.carport lts. total 5880 watts 5880
5.room lts. 500 watts 500
6. gen recpts. x2 1500 watts ea. 3000
total 55,436 VA
first 10,000va @ 100% 10,000
remainder of 45,436 @ 40@ 18,174.40
total 28,174.40 VA / 240V
117.39 Amps
Am I on the right track here? Thanks, sparks