Load calculation of multiple VFD driven motors

Status
Not open for further replies.

Electriman

Senior Member
Location
TX
Greetings,

I was wondering if NEC 220.50, 430.24, 430.25, 430.26 is applicable to size a feeder that feeds a combination of direct driven motors and and VFD driven motors.

Thanks in advance
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Are you only thinking of the conductors?

430.26 would apply to AHJ discretion, so unless you have that, ignore it. 430.25 applies to factory listed equipment, otherwise you use 430.24. So really, 430.24 is what applies. What I did was apply 430.122 (125% of the VFD INPUT current rating, not the motor) if that was the largest load, then follow the rest of the rules accordingly.
 