Rolson
- Sioux falls
I had some questions regarding this image from a Mike Holt video. Now according to NEC 2014 a number 12 copper wire at 60C is rated at 20amps. So how can you carry at 23 amp load on this 20 amps worth of wire. After following the note to 240.4 (D) we see
Also according to the code section 240.4 (D) After all correction factors are taken into account a 12AWG must not exceed 20 amps unless stated in 240.4 (E) or (G). E should have no effect unless it is a tap situation. So that leads up to 240.4 (G) which states
That the code can be altered for air condition equipment and refer to 440 parts 3 and 4 which states
We must have some more information on the problem but also we must have 125% for our branch circuit conductors so that 23 must be sized to 28.75.
On another code section that should be taken into account would be 110.14 (C) (1) which talks about electrical connections and temperature limitations. The code states "The temperature rating associated with the ampacity of a conductor shall be selected rating of any connected termination, conductor, or device. Conductors with the temperature rating higher than specified for terminations shall be permitted to use for ampacity adjustment, correction, or both."
Still on the same code section it states unless all the equipment is "listed or marked" the conductors should be sized off of 310.15 (B)(16). Also a termination provision of equipment 100 amps or less or marked 14AWG-1AWG should be sized off of the 60C column unless it marked differently as above in 110.14(C) or some exceptions that are not related to this.
If it over 100amps or bigger than 1AWG you can use the 75C column.
So where is this 25amps on 12AWG at 60C coming from?