Load calculation

Status
Not open for further replies.

johnjohnls.js

Member
Location
US
I need to add 2 100A electrical vehicle charging stations. Im not sure how to calculate wether my service can handle them.

Sent from my LGMP260 using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
A little detail on what you are adding these circuits to will help a lot.

Chances of adding them to a large commercial or industrial facility is much greater at having needed capacity than a small older dwelling that maybe still has a 60 amp service run to it.

Then next thing is 100 amps what they actually draw from supply, maximum branch circuit capacity, etc.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
220.16(B) which will take you back to 220.14(A).

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Some of those units can communicate with each other so that only one charges at a time. There are also 3rd party controls that can do the same.
 