load calculation

Status
Not open for further replies.

steveng

Senior Member
Location
Texas
need help on this calc,

100 va xfmr can handle what load on 24vac
100 va xfmr can handle what load on 12 vac

100/24=4.1a secondary
100/12=8.3a secondary

120/100=.83a primary

am i reading this correct?;)
 
steveng said:
need help on this calc,

100 va xfmr can handle what load on 24vac
100 va xfmr can handle what load on 12 vac

100/24=4.1a secondary
100/12=8.3a secondary

120/100=.83a primary

am i reading this correct?;)
Yes, except you have a typo. You should have 100/120 = 0.83a primary.
 
080623-0618 EST

steveng:

Your calculations are correct except that the third one should be written as
100/120 = 0.83
The primary current will be somewhat higher because of transformer losses.

.
 
gar said:
080623-0618 EST

steveng:

Your calculations are correct except that the third one should be written as
100/120 = 0.83
The primary current will be somewhat higher because of transformer losses.

.

thanks guys, for the replies!!!

gar, would you use a 1.0a primary fuse to protect this circuit?


Actually, you have windings in parallel or series. Power is conserved.

Ppri = Psec; P = VI
VpriIpri=VsecIsec = 100[/B can you elaborate on this?
 
080624-2212 EST

steveng:

Use a slow-blow, but its value will depend upon the actual load and inrush current. I also might use a negative temperature coefficient thermistor to reduce inrush current.

I never understood the purpose of the comment on series and parallel and how it related to your question.

.
 