I've got a project under construction with a few water source heat pumps that where spec'd with integral backup heat strips. The designer on the project picked up the full load (heat pump + heat strip), but didn't catch that the heat strips are only for backup and that the manufacturer requires a separate circuit for them (one circuit for the heat pump & one for the heat strip) at each unit.
Now we have 110A circuits installed to each of the units that actually require two 50A circuits to each. To complicate things a little more, each of these units are mounted up high (not accessible).
I'm about to recommend that the contractor install a small load center at each unit with two breakers in each to feed the unit and the heat strips separately. According to 240.24(A)(4) this would simply be overcurrent devices adjacent to utilization equipment, so the load center would not be required to be accessible. Am I missing anything?
Now we have 110A circuits installed to each of the units that actually require two 50A circuits to each. To complicate things a little more, each of these units are mounted up high (not accessible).
I'm about to recommend that the contractor install a small load center at each unit with two breakers in each to feed the unit and the heat strips separately. According to 240.24(A)(4) this would simply be overcurrent devices adjacent to utilization equipment, so the load center would not be required to be accessible. Am I missing anything?