Load Center grounding

Status
Not open for further replies.

laketime

Senior Member
I installed a new load center in a barn. Installed the ground rods as well. Do the grounds in the load center land with the neutrals or do I need to install a separate ground buss?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If you ran an EGC with the feeder (required under the 2008) the neutral(s) and EGC(S) must be seperated.

Roger
 