laketime Senior Member Aug 4, 2010 #1 I installed a new load center in a barn. Installed the ground rods as well. Do the grounds in the load center land with the neutrals or do I need to install a separate ground buss?
I installed a new load center in a barn. Installed the ground rods as well. Do the grounds in the load center land with the neutrals or do I need to install a separate ground buss?
roger Moderator Staff member Location Fl Occupation Retired Electrician Aug 4, 2010 #2 If you ran an EGC with the feeder (required under the 2008) the neutral(s) and EGC(S) must be seperated. Roger
If you ran an EGC with the feeder (required under the 2008) the neutral(s) and EGC(S) must be seperated. Roger