Load center located in bathroom

Status
Not open for further replies.

drickert

Member
NEC Section 230.70 A (2), states that "Service disconnecting means shall not be located in bathroooms." Is there also a code prohibiting the installation of a loadcenter in a bathroom? I can't seem to locate it in the NEC.
 
Re: Load center located in bathroom

240.24e, prohibits the installation of overcurrent devices in bathrooms of dwelling units and guest rooms of hotels and bathrooms.
 
Re: Load center located in bathroom

Bare in mind that only in dwelling units is this prohibitted. It is perfectly legal to put one in a commercial bathroom, but working clearance issues often seem to pop up.
 
Status
Not open for further replies.