Load center location

Status
Not open for further replies.
I'm drawing a blank. I have an existing subpanel in a TI that is a wall that is to be demo'ed. The wall we are looking into for the relocation has a sink on it. Besides clear work space per 110.26 is there a specific requirement about how far away it needs to be from the edge of the sink?

It seems like there should be but I can't think of what.
 
Besides clear work space per 110.26 is there a specific requirement about how far away it needs to be from the edge of the sink?

It seems like there should be but I can't think of what.

No, there is no NEC required minimum distance a panel must be kept away from a sink.

Chris
 