What happens if the parallel running generators do not share the loads proportionally?
Why is it necessary to share the loads in proportion to their ratings? or equal sharing in case of similar generators?
The risk is that one generator will be overloaded. If one generator can carry the entire load, this isn't as big an issue, but then you don't really need two generators.What happens if the parallel running generators do not share the loads proportionally?
Say, there are two generators of 15MW and a total load of 25MW, If one generator shares a load of 15MW and other one shares 10MW. Essentially, the generators are loaded within their ratings, but not sharing the loads equally between them.
In this case, Is there a problem?
Your comment would indicate not a parallel in the scenes that I would see for parallel from the utility. That just always split evenly the load between the feeders of a parallel service or more accurately load applied across all conductors of the parallel.Say, there are two generators of 15MW and a total load of 25MW, If one generator shares a load of 15MW and other one shares 10MW. Essentially, the generators are loaded within their ratings, but not sharing the loads equally between them.
In this case, Is there a problem?