J jjsparky Member Location Westminster, Colorado, USA Occupation Superintendent I/E Sep 14, 2022 #1 When do you have to do 250.102(D)? (load side bonding), As i look through the code it is not clear to me when it has to be done.
When do you have to do 250.102(D)? (load side bonding), As i look through the code it is not clear to me when it has to be done.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Sep 14, 2022 #2 If you have a 480 volt disconnect switch with concentric KO's there would need to be a bonding jumper around the KO's on the load side. That would be sized according to the OCPD in T250.122.
If you have a 480 volt disconnect switch with concentric KO's there would need to be a bonding jumper around the KO's on the load side. That would be sized according to the OCPD in T250.122.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 14, 2022 #3 250.96, 97, 98, and 100 list some of the area where bonding is required and, at times, require a wire type bond jumper.
250.96, 97, 98, and 100 list some of the area where bonding is required and, at times, require a wire type bond jumper.
J jjsparky Member Location Westminster, Colorado, USA Occupation Superintendent I/E Sep 16, 2022 #4 Thanks for your replies.