load side bonding 250.102(D)

Status
Not open for further replies.
If you have a 480 volt disconnect switch with concentric KO's there would need to be a bonding jumper around the KO's on the load side. That would be sized according to the OCPD in T250.122.
 
250.96, 97, 98, and 100 list some of the area where bonding is required and, at times, require a wire type bond jumper.
 