Load Side Connection to Main Breaker

Status
Not open for further replies.

NEC User

Senior Member
There is an existing 2-pole 240V 100Amp main circuit breaker and corresponding enclosure which feeds a toll plaza. I need to feed proposed roadway lighting. Are my able to tap proposed power cables for the roadway lighting directly to the load side of the existing main breaker. In this configuration, power cables for the roadway lighting and existing toll plaza will both be connected directly to the load side of the existing main breaker.
 
There is an existing 2-pole 240V 100Amp main circuit breaker and corresponding enclosure which feeds a toll plaza. I need to feed proposed roadway lighting. Are my able to tap proposed power cables for the roadway lighting directly to the load side of the existing main breaker. In this configuration, power cables for the roadway lighting and existing toll plaza will both be connected directly to the load side of the existing main breaker.

you need to determine the existing load on the 100A breaker, then determine the new lighting load. If the main breaker is large enough to accommodate the total load then yes, with the assumption that the new lighting cable is rated for at least 100A.
 
Thanks, I was considering installing a terminal block after the main breaker and splice accordingly. Out of curiosity, how man cables can I connect directly to a 100A main breaker? I supposed I'd have to verify with the manufacturer. Square D told me I can only install one phase A and one Phase B to a 2 pole breaker and that if I wanted more, I'd have to splice at some point after the breaker.
 
Thanks, I was considering installing a terminal block after the main breaker and splice accordingly. Out of curiosity, how man cables can I connect directly to a 100A main breaker? I supposed I'd have to verify with the manufacturer. Square D told me I can only install one phase A and one Phase B to a 2 pole breaker and that if I wanted more, I'd have to splice at some point after the breaker.

They got some pretty smart fellas there at Sq D.:):)
 