load side grounded circuit conductor

Merry Christmas
Status
Not open for further replies.

tower

Member
Location
Massachusetts
250.142(b)exception 2. could you show me an example where you would install the meter on the load side of the service disconect. or if anything, could you clarify this exception,exspecialy (a) & (b) of exception #2
 

rickg

Member
Location
Rhode Island
Re: load side grounded circuit conductor

Our POCO requires cold sequence metering on 277/480 volt services, (disco ahead of meter). I imagine that this is true for all of National Grid (RI, Mass, part of NH).
 