Load side of generator ATS

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
Load side of generator Auto Transfer Switch (ATS) has feeder cables going to the panelboard. Is the panelboard require to have main circuit breaker to protect the feeder cables from the ATS based off of NEC 2014?

Sent from my SM-G935U using Tapatalk
 
No, you can use MLO (unless its a funky set up and its a feeder tap). The feeder would be protected by the Breaker in or ahead of the transfer switch (ignore the academic case of if the ATS was the service disconnect and did not have overcurrent protection built in).
 