Forum,
Long time reader - first time poster. I was wondering if anyone has any citations for some common sense reasoning that can be founded in a formal statement from either the IEEE or the NEC. I have not found any such details to date.
I have a situation where existing 'as-built' electrical plans and equipment schedules are not readily available for some facilities. It is desired to add new cord-and-plug connected load that will draw up to about 4A on a non-continuous basis, and perhaps 1A on a continuous basis.
The impact of such loading is akin to that of plugging in various consumer electronic devices to general outlet receptacles. However, it seems difficult to formally qualify that a full and complete load-study, from the point of connection all the way back to the service entrance, is unnecessary.
A further point is that for any load addition, the existing load has to be determined in accordance with NEC 220.87 so that adequate headroom can be verified. If this is to be done via 30 day metering (per the 220.87 exception), then the load-metering study surely has to be applied on every feeder and panel affected by the increased burden - all the way to the service entrance (right?). Just because one panel is not overloaded makes no guarantees about upstream supply panels and feeders. For such a small load, this seems incredibly and unnecessarily complex, especially on services that are as large as 1600A @ 480V, for instance.
Has anyone run into such a situation before? Common sense intuition needs to be substantiated with some codified or detailed engineering guideline or requirement from a recognized body such as the IEEE or NFPA.
Thanks,
Brendan.
Long time reader - first time poster. I was wondering if anyone has any citations for some common sense reasoning that can be founded in a formal statement from either the IEEE or the NEC. I have not found any such details to date.
I have a situation where existing 'as-built' electrical plans and equipment schedules are not readily available for some facilities. It is desired to add new cord-and-plug connected load that will draw up to about 4A on a non-continuous basis, and perhaps 1A on a continuous basis.
The impact of such loading is akin to that of plugging in various consumer electronic devices to general outlet receptacles. However, it seems difficult to formally qualify that a full and complete load-study, from the point of connection all the way back to the service entrance, is unnecessary.
A further point is that for any load addition, the existing load has to be determined in accordance with NEC 220.87 so that adequate headroom can be verified. If this is to be done via 30 day metering (per the 220.87 exception), then the load-metering study surely has to be applied on every feeder and panel affected by the increased burden - all the way to the service entrance (right?). Just because one panel is not overloaded makes no guarantees about upstream supply panels and feeders. For such a small load, this seems incredibly and unnecessarily complex, especially on services that are as large as 1600A @ 480V, for instance.
Has anyone run into such a situation before? Common sense intuition needs to be substantiated with some codified or detailed engineering guideline or requirement from a recognized body such as the IEEE or NFPA.
Thanks,
Brendan.