I have a 3 phase panel. The A phase reads at 78.84 the B phase reads 61.19 and the C phase reads 50.14 amps. Does this mean that the load at the time of the reading is the three combined for a total load amps of 190.17 ?
Does this mean that the load at the time of the reading is the three combined for a total load amps of 190.17 ?
I have a 3 phase panel. The A phase reads at 78.84 the B phase reads 61.19 and the C phase reads 50.14 amps. Does this mean that the load at the time of the reading is the three combined for a total load amps of 190.17 ?
You are too kind.I predict that a lecture from charlie b is fast approaching.![]()
After the combination your reference to previous postings #3 and #5 do not make sense. Do you mean #3 and #7?I have combined the two threads into one, since we do not allow duplicate threads.
Yes. I have made the correction. Many thanks.After the combination your reference to previous postings #3 and #5 do not make sense. Do you mean #3 and #7?
Gar -090115-1322 EST
Adding the magnitude of the three currents is not necessarily meaningless.
Suppose the entire load is resistive, it is a Y system, and the neutral is connected.
I said "total load amps" is a meaningless number.Adding the magnitude of the three currents is not necessarily meaningless.
Now you are changing the OP. But my post is still valid.gar said:Suppose the entire load is resistive, it is a Y system, and the neutral is connected.
jim dungar said:The only time you would add them is when you have several conductors that combine into a single conductor
090115-1322 est
adding the magnitude of the three currents is not necessarily meaningless.
Suppose the entire load is resistive, it is a y system, and the neutral is connected.
Then as an approximation --- the total load power assuming a balanced source voltage is
power total = vline to neutral * (iline1 + iline2 + iline3).
Make it a delta load load and it is still
power total = vline to line * (iline1 + iline2 + iline3) / sq-root of 3.
.
Power total = Vline to line * (Iline1 + Iline2 + Iline3) / Sq-root of 3.
p= sqrt(3)*{[(v1*i1)+(v2*i2)+(v3*i3)]/3}
In the world of magnitude-only approximations...
sqrt(3)*{[(v1*i1)+(v2*i2)+(v3*i3)]/3} = Vline to line * (Iline1 + Iline2 + Iline3) / Sq-root of 3So what's your point?
Allowance for voltage diferences. Duh.......![]()