loadcenter / panelboard for 240 Delta

Status
Not open for further replies.

wireguru

Senior Member
Can a sqd QO or NQ panel be used on 240v delta (corner grounded I believe, not a 120/240 high leg service)? Or only 120/240 or 120/208 systems?
 
If I read the website catalog correctly, NO.
The panels are listed for 1ph 3 wire or 3 pahse 4 wire and the branch breakers listed are slash-rated
 
If I read the website catalog correctly, NO.
The panels are listed for 1ph 3 wire or 3 pahse 4 wire and the branch breakers listed are slash-rated


Actually I just looked at the catalog, and QO is rated for the following uses

120 Vac, 1φ2W •
240/120 Vac delta, 3φ4W
120/240 Vac, 1φ3W •
240 Vac corner grounded delta, 3φ3W
240 Vac delta, 3φ3W •
208Y/120 Vac, 3φ4W
48 Vdc maximum (1φ convertible main lug 12–4 2 circuit only)


heres the link
http://ecatalog.squared.com/pubs/El...rs/QO Three Phase Load Centers/1100CT0501.pdf
 
glad you looked.... I thought I had, but obviously I did not look far enough. Thanks. (don't forget 240.85)
 