weressl
Esteemed Member
I think that the vector diagram here is more correct in the HYPOTHETICAL depiction of what is happening. The phase angle of adjacent phases are always 120* if each phase has the same power factor.Thanks for the diagram. I am still waiting for the engineers answer.
I'm having trouble seeing where you are getting your angles for the load currents which you are adding vectorally to get the line current. I know all of the vectors are the L-L currents with their respective angles but I'm not seeing where you are getting the angles. Can you please explain? From looking at it, it appears that the L-L current angles are 30deg phase shifted from normal L-N currenat at 0,120,and 240?
We do not know that is the power factor of the rectifiers, but we know it's lousy. Unless the load diagram depicts kW loads it is immaterial if we only try to look at amperes. The phase-to-phase relationship will not change on a single phase load. The large loads are the rectifiers and they are connected between two phases. Assuming that the 45kVA load is a transformer and that the loads are balanced in each phase and also assuming that the rectifiers have a 30* angle worse power factor than the transformer then the following vector diagram is applicable.