As I said before, I'm not 100% sure, but I don't see anything in the code that supports what you are saying. I think the extra 25% on all units is required.
See 430.24
As I said before, I'm not 100% sure, but I don't see anything in the code that supports what you are saying. I think the extra 25% on all units is required.
See 430.24
But that's for motors, and we are talking RTU's that include electric heat.
yeah, it's my understanding that the MCA, as calculated and published by the mfg, includes all of the loads + 25% of the largest motor. I have always presumed that it included 125% of the heater load.
And if the unit is heating and cooling at the same time (which is very likely in a restaurant in Florida), ALL of the loads just might be simultaneous.
thanks!
Well it depends on the chassis design as far as the sequence of airflow. If it passes through heater before the AC, dehumidification is practically impossible and it pretty much guarantees the two won't operate together.
If AC comes first, it's possible to dehumidify, then reheat but I don't know if that is actually done given how incredibly inefficient it is.
If it passes through heater before the AC, dehumidification is practically impossible and it pretty much guarantees the two won't operate together.
If AC comes first, it's possible to dehumidify, then reheat but I don't know if that is actually done given how incredibly inefficient it is.
430.24 is for Several Motors or Motor(s) and Other Load(s). An RTU with electric heat fits that definition.
But when I look at it again, it says 125% of the largest motor, plus 125% of the continuous loads, and heat is a continuous load per 424.3.
Each is describing different situations, 424.3(B) is referring to to branch circuits for fixed electric space heating.But when I look at it again, it says 125% of the largest motor, plus 125% of the continuous loads, and heat is a continuous load per 424.3.
Each is describing different situations, 424.3(B) is referring to to branch circuits for fixed electric space heating.
430.24 is a motor or several motors and other loads and is talking about a common conductor supplying such loads.
If you are calculating a service or feeder - you need to know the largest motor plus all other loads that can run simultaneously to get the minimum allowable conductor ampacity.
But when I look at it again, it says 125% of the largest motor, plus 125% of the continuous loads, and heat is a continuous load per 424.3.
Heat is NOT a continuous load per 424.3. 424.3 says fixed electric heating shall be CONSIDERED a continuous loaf for the purposes of BRANCH CIRCUIT SIZING.
424.3 has no impact on feeder sizing.
take a look at exception 2 to 430.24.
That refers back to 424.3B. More evidence for my side of the argument.
The Title of section 424.3 is BRANCH CIRCUITS
The Title of subsection 424.3(B) is BRANCH CIRCUIT SIZING
A feeder is NOT a branch circuit. 424.3(B) does NOT apply to feeders.
The handbook is not the Code. 215.3 doesn't say anything about electric heat.Sure, but both the handbook and 215.3 seem to indicate that this still has a direct effect on the feeder or service sizing.
Isn't deciphering NEC fun sometimes?That refers back to 424.3B. More evidence for my side of the argument.