Need some opinions on a new Generator and a Service rated ATS install
This is a new install of a 502kw gen at an existing super market
Because of down time necessary for setup
Space is very tight for clearance and working space and equipment
We had to put up a new Ct cabinet for new overhead service drop
in order to leave existing underground service on till switch over.
Out of the Ct we need to get to the new Service rated nema3 ATS
come out to the generator and also to the MDP located inside the building.
Bottom of the Ats is a space of 36"x 24" for pipe entrance
We are looking at 12 -4 " pipes in this space ( not much space)
by the looks of the cabinet i would guess it was a nema 1 with a roof kit added and door extension kit added to turn it into a nema 3
(Poor design Square-D)
My question is can we have a local shop make us a spit 2 level wireway/trough
with 2 doors on sides so we can just layin on our 500's
Split level for service conductors on top , load and gen. on bottom level
in a T shape with ct on left, ats middle, and pipe to mdp out on right.
Can a shop fabricate this up with the proper gauge and corrosion metal,
without a UL listing , but approved by POCO and AHJ ?
Can we cut and enter the side of the Ats removable panel with a flanged and gasket kit?
Will try to post some pics and video's tomorrow