gman

Member
Location
Idaho
In a remodel I am working on the only logical place we can place the indoor main panel is on the outside wall which is also part of a basement stair landing. The outdoor meter entrance will be located approximately 24" above then dropped down through the wall in conduit. Does the NEC have anything in regards to locating a main panel on a stair landing wall?

Thank you ahead of time,

G
 
A

a.wayne3@verizon.net

Guest
Re: Locating a Main Panel on a Stair landing?

I`ve looked but can`t find a referance to this in 2002 code,Is there working clearance???????
 

bphgravity

Senior Member
Location
Florida
Re: Locating a Main Panel on a Stair landing?

I agree with a.wayne. Make sure you have working clerance and proper OCD accessiblity. :)
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: Locating a Main Panel on a Stair landing?

Your inspector will probably use "working spaces" to fail you.

How would you install and/or protect the homeruns?

Could you install a disconnect and locat the panel in another location.

I can invision an application where you could do this, however I do not like it.

If and only if there was no other way and you could stand on the landing and work safely on the panel, I would use 90.2(C).
I mean 90.4.
Mike P.

[ April 23, 2003, 09:30 AM: Message edited by: jxofaltrds ]
 

gman

Member
Location
Idaho
Re: Locating a Main Panel on a Stair landing?

The landing is approximately 4'x8' with plenty of clearance. It is four steps down from the main floor and four steps up from the basement floor.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Locating a Main Panel on a Stair landing?

As long as the landing provides the required work space in front of the panel there is no code section that can be cited to fail the installation.
Don
 

gman

Member
Location
Idaho
Re: Locating a Main Panel on a Stair landing?

Thank you for the replys. I think the only thing he can ding me on would then be the distance the meter is from the main panel, but I think I can bounce around that by encasing the mains in GRC to protect them from someone driving a nail through them to hang a picture.
 

bill addiss

Senior Member
Re: Locating a Main Panel on a Stair landing?

gman,

Just a thought
Is there a light over the landing?
That might be something that could bite you too.

Bill
 

gman

Member
Location
Idaho
Re: Locating a Main Panel on a Stair landing?

Spoek with the inspector and he required at least 3 feet of room in front of the main panel. He mentioned nothing about a light under the stairs. Bill how might that effect things?
 

bill addiss

Senior Member
Re: Locating a Main Panel on a Stair landing?

gman,

I mean a light over the stairs, not under them.

You didn't mention what type of occupancy this was, but in a Dwelling unit a light would be required in the stairway per 210.70(A)(2) and also in a Basement near equipment requiring servicing per 210.70(A)(3).

And, 110.26(D) requires illumination be provided for working spaces about service equipment at 600V or less in all occupancies.

Bill

[ April 24, 2003, 12:11 AM: Message edited by: bill addiss ]
 

gman

Member
Location
Idaho
Re: Locating a Main Panel on a Stair landing?

Bill this is basically a three story dwelling including the basement. The stair landing is located under the stairs that lead to the second floor and four steps down from the gound floor leading to the basement. It will be illumiated since it is it leads to their family room located in the basement.
 