No. A lock at the source does not change the need to troubleshoot at the disconnect.Would a breaker lock out fix this
Don
No. A lock at the source does not change the need to troubleshoot at the disconnect.Would a breaker lock out fix this
Well thats what i have an inspector wanting because work space can not be met.If it makes him happy we will give him onedon_resqcapt19 said:No. A lock at the source does not change the need to troubleshoot at the disconnect.
Don
infinity said:Well said Don. I think of all of the AC units, VAV's, and fan power boxes that are installed above hung ceilings in commercial buildings. These things never have the required clearances. Anyone who has had to wire one using a mirror because the access panel faced an I-beam or a piece of ductwork will tell you that 110.26 is a farce.
cpal said:Any one who has ever had to service on of those cramped units is swearing at the wiring inspector for not enforcing 110.26.
I see it all the time (when another permit is filed) the original electrician installs the disconnect for a final in December (plenty of clearance) and in June the HVAC people drop the units in front of the disconnect.
There has to be a break point where there is some communication between the disiplines .
Jim W in Tampa said:Yes and its the inspectors that could make this happen.Start red tagging and the two will start to work this out.If Mr AC sets his unit in front of my disconnect i would make him move it.
mpd said:440.14 only requires the disconnect to be readily accessible, 110.26 does not apply, the problem is 440.14 will allow many interpretations
Would love to have a copy of that letter as its just starting to be pushed here.mpd said:I always enforced 110.26 for air cond. disconnects, a contractor challenged me on it, and I was told by the state I work in that they had got an interpretation from NFPA and 440.14 applies to air cond. disconnect, and I could not cite 110.26 for an air cond. disconnect.
In my opinion, this is a responsibility of the GC.cpal said:There has to be a break point where there is some communication between the disiplines.
mpd said:I always enforced 110.26 for air cond. disconnects, a contractor challenged me on it, and I was told by the state I work in that they had got an interpretation from NFPA and 440.14 applies to air cond. disconnect, and I could not cite 110.26 for an air cond. disconnect.
It is but he wont push it unless the inspector does.Want to see this change ? It has been violated for more than the 25 years i been wiring.Red tag it and it will stop real fast.Dont tag it and nothing will ever change.LarryFine said:In my opinion, this is a responsibility of the GC.
What I mean is: the GC is the one who is supposed to coordinate the different contractors, and to make sure that, for example, when the HVAC comes back later, he doesn't cause a problem with pre-existing equipment. The GC should make the HVAC guy move the unit.Jim W in Tampa said:It is but he wont push it unless the inspector does.
LarryFine said:What I mean is: the GC is the one who is supposed to coordinate the different contractors, and to make sure that, for example, when the HVAC comes back later, he doesn't cause a problem with pre-existing equipment. The GC should make the HVAC guy move the unit.
Does the disconnect have any fuses or circuit breakers in it? If not, the clearence requirements in 110.26 do not apply in regards to working clearences.Dennis Franklin said:Hi everyone.... Just received a correction notice for having the outside disconnect for a slab-mounted ac unit for a residence located on the wall just over the edge of the ac unit, above it about 4 feet from the ground. The inspector quoted article 110-26 II for the violation. I used article 440.14 for determining the location. Whichof these articles apply to residentual ac units, mounted outside the residence on the ground??? Thanks for your help, gotta get these new inspectors trained!!! Dennis Franklin in New Mexico
McDowellb said:Does the disconnect have any fuses or circuit breakers in it? If not, the clearence requirements in 110.26 do not apply in regards to working clearences.