I am working on a new wing of a hospital in southern California. There are new roof mounted, mushroom type, exhaust fans, with manufacturer installed switches under the top cover. A screwdriver is required to access the switch. The OSHPD Inspector is requiring an additional disconnect switch to be installed on the outside of the fan enclosure. I believe that the supplied switch is "code compliant" and satisfies the required, motor disconnecting means. Per NEC 404.8 exc#2, switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than 2.0m and shall be accessible by portable means. NEC 430.102(B) states that, a disconnecting means shall be located in sight from the motor location and the driven machinery location.
I feel that we are installed per code and need some help convincing the Inspector otherwise.