250.52(b) describes a ground rod (electrode). 250.53(G) states that the ground rod shall have 8 feet of contact with soil and that the top is to be below grade unless the attachment (clamp) is protected. 250.10 states that the clamp can be protected or rated for no protection.
Is there a section that states that the grounding electrode must be outside the footprint (or foundation) of the structure?
We had a repair where the entire house is surrounded by concrete. The HO opted to bore holes in the garage slab (near panel) to install ground rods. AHJ says that rods must be outside.
Is there a section that states that the grounding electrode must be outside the footprint (or foundation) of the structure?
We had a repair where the entire house is surrounded by concrete. The HO opted to bore holes in the garage slab (near panel) to install ground rods. AHJ says that rods must be outside.