Re: Location of Service Main Disconnect
NEC:
230.3 One Building or Other Structure Not to Be Supplied Through Another.
Service conductors supplying a building or other structure shall not pass through the interior of another building or other structure.
NEC Handbook:
Service conductors are permitted to be installed along the exterior of one building to supply another building. However, service conductors supplying a building are not permitted to pass through the interior of a building. Each building served in this manner is required to be provided with a disconnecting means for all ungrounded conductors, in accordance with Part VI, Service Equipment?Disconnecting Means.
For example, in Exhibit 230.14, Building No. 2 service is not to be supplied through Building No. 1 service. The service disconnecting means shown for Building No. 1 and Building No. 2 are located on the exterior walls. A disconnecting means suitable for use as service equipment is required to be provided for each building.
Let me make it clear at that the deed to the second house changed hands at the time of the daughters marriage.
Tom
I have seen services as you described at state parks. I never inspected a service for cabins at state parks, and I would have assumed these buildings were under control of one owner on the states property. I will have to look into this more.
In the handbook illustration combined with the commentary it is clear that the author is saying the service conductors to the second building have to stay on the exterior of the first building.
I read the rule to first say one building or structures service shall not be supplied through another.
Second I read the rule to also say that the service conductors of the second building cannot pass through the first building.
you say because the conductors entering the first building are service conductors and because they leave the first building as feeders, (after passing through a service disconnect) to the second building, the service conductors have not passed through the first building.
You still cannot get away from the second building service being supplied through the first building.
The rule does not address feeders and the rule does not address service conductors alone. the rule addresses a building service as a whole