The advice so far is on target, and about all I can offer is to expand on what has already been said. It is a UL issue as Ron stated, rather than a NEC issue. Article 285 specifies the minimum installation requirements and minimum KIAC withstand ratings, not where, when, or if they should be used at all. That is a design issue. If design and TVSS info is what you are after obtain copies of UL 1449 Second Edition, UL 1283 cUL, ANSI/IEEE C62.41 ? 1991, C62.45 ? 1995, NEMA LS-1 ? 1992
For new installations the best solution if the service is single phase and equal to or less than 200-amps is to have the local POCO install a device at the meter socket, or buy your panel(s) with a TVSS device built into the unit. The reason is as Wayne (aka hurk27) stated if the leads are longer than 6 inches the TVSS is rendered useless.
I have not personally used the breaker types as of yet. I suspect these are small class "A" devices with either MOV's or SAD's but not both (size would be limited). I am not sure how difficult it would be to test or monitor them either. However they have possibilities if used as class "A" and possible class "B" devices in sub-panels.
What ever method you use, be sure it is UL-1449 listed with a SVR rating of 330 on a single phase system, and per ANSI/IEEE C62.41-1991 and ANSI/IEEE C62.45-1992. Avoid units with L-G, and N-G modes at the service entrance locations.