Working on a house where the telephone company installed the NIU with integrated primary protector on the streetside elec. service pedestal. Telephone service will then run through dedicated underground PVC conduit to house about 75 feet away. Shielded cable with shield grounded at both ends will be used.
Question for this august group is whether an additional primary protector is required at the point of entrace to the house. 800.90 (B) says the primary protector on the circuit must be in, on, or adjacent to the building or structure served. Is the pedestal considered to be that structure? If so, the subsequent run to the house is an interbuilding circuit that per 800.90 (A) doesn't require a primary at each end if less than 140' in length run underground using shielded cable. Or is the house itself the structure, which would require a much closer protector?
Thanks in advance
Skip
Question for this august group is whether an additional primary protector is required at the point of entrace to the house. 800.90 (B) says the primary protector on the circuit must be in, on, or adjacent to the building or structure served. Is the pedestal considered to be that structure? If so, the subsequent run to the house is an interbuilding circuit that per 800.90 (A) doesn't require a primary at each end if less than 140' in length run underground using shielded cable. Or is the house itself the structure, which would require a much closer protector?