Can the heat strip be locked out when on generator power using 2-pole mechanically held contactor inside AHU? 
Configuration: 400A service w/(2) 200A panels...(1) 200A panel will be emergency power panel w/30KW generator.
Upon generator start up would like to lock out just the 10kw heat strips in (2) AHU's but need power to AHU for blower.
Any suggestions?
	
		
			
		
		
	
				
			Configuration: 400A service w/(2) 200A panels...(1) 200A panel will be emergency power panel w/30KW generator.
Upon generator start up would like to lock out just the 10kw heat strips in (2) AHU's but need power to AHU for blower.
Any suggestions?
 
				