chevyx92
Senior Member
- Location
- VA BCH, VA
When do you have to figure in the LRA when determining circuit conductor ampacity? Motors are not my forte. Here's what I have. Motor Nameplate: 25HP, 74 A, Volts 208, 3 Phase, Service Factor 1.15, Code F, Design B. Table 430.250 of the 2005 code gives me 74.8A. So I get 74.8 x 125%= 93.5 Amps to size my circuit conductors. Correct? And then for overcurrent protection (inverse time breaker) I get 74.8 x 250%= 187A, next higher setting is 200 Amp. Have I done this right? Do I need to worry about LRA in my calcs? Thanks.