And I maintain the LRCs provided by the NEC take this into account just like the FLC tables in 430 are based on worst case scenario.
The LRC table would be worthless in sizing OCPDs if that was not so.
I kind of agree with you - but only when sizing an OCPD for across the line starting, throw in reduced voltage starting or a soft starter and you likely find lower OCPD setting in most installations then you would see if it were across the line started. I just am not seeing the NEC addressing the issue of a reduced voltage starting method for a fire pump being required to be able to have overcurrent protection sized to be able to start across the line should the reduced voltage method happen to fail. The switches and contactors maybe still need to meet worst case scenario, but trip setting could be anywhere as far as art. 430 tables are concerned.