Locked rotor starting current

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
I’m trying to determine if the Client specification needs to be revised. They want the MCP settings from 700% to 1300% (460V induction motors) and motor locked rotor must not exceed code G per NEC T430.7(B). Is this realistic? Would it be better to have the range up 1700% (per NEC exception) in case they have a Design B or E high efficiency motor? Is that even possible for Code G?
We’re focusing on 15HP motors (up to 100Hp).
Is it likely the MCP will trip with Code G when set at its maximum setting of only 1300%?


Sent from my iPhone using Tapatalk
 

EC Dan

Senior Member
Location
Florida
Occupation
E&C Manager
LRA for type G 15 HP 460 V motor would be 106-119 A. The MCP range at 700-1300% for a 15 HP 460 motor would be 147-273 A. If anything, seems like the MCP is oversized.

Edit: I take back my last comment, the MCP is sized appropriately for 800% of FLA.
 
Last edited:

Dale001289

Senior Member
Location
Georgia
LRA for type G 15 HP 460 V motor would be 106-119 A. The MCP range at 700-1300% for a 15 HP 460 motor would be 147-273 A. If anything, seems like the MCP is oversized.

Edit: I take back my last comment, the MCP is sized appropriately for 800% of FLA.

How did you determine the max 119A?


Sent from my iPhone using Tapatalk
 

EC Dan

Senior Member
Location
Florida
Occupation
E&C Manager
Max KVA/HP for type G = 6.29 based on table 430.7(B)
LRA = 6.29 * 15 * 1000 / (460 * 1.73) = 119
 

Dale001289

Senior Member
Location
Georgia
Max KVA/HP for type G = 6.29 based on table 430.7(B)
LRA = 6.29 * 15 * 1000 / (460 * 1.73) = 119

Thanks Dan.
Would happen to know if this range, i.e. LRA G, restricts motor selection to certain NEMA design motors, such as A, C and D? What about high efficiency Design B?
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
FWIW most of the cage motors I have experience with have been around 6PU (600%)
Mostly 30kW upwards.
 

EC Dan

Senior Member
Location
Florida
Occupation
E&C Manager
Thanks Dan.
Would happen to know if this range, i.e. LRA G, restricts motor selection to certain NEMA design motors, such as A, C and D? What about high efficiency Design B?

Not sure exactly, but I found this source which indicates designs B-D are compatible with up to code J motors for a 15 HP 460 V motor, and anything higher would typically be a design E motor:

1638543723287.png
 

Dale001289

Senior Member
Location
Georgia
Not sure exactly, but I found this source which indicates designs B-D are compatible with up to code J motors for a 15 HP 460 V motor, and anything higher would typically be a design E motor:

View attachment 2558575

Nice research. My understanding is Design E motors are very rare. Looks like LRA code G will cover the vast majority of motors. Thanks again.


Sent from my iPhone using Tapatalk
 