There have been misapplications of motor protection. Most people don't care because in general it is cheaper to replace a small motor than it is to protect it correctly. It is also a common practice to size branch circuit devices at the maximum allowed setting rather than coordinating them with the motor damage curve and the OL relay curve.
OL relays are usually set for 600% at 10 sec for a fast trip and 20 sec for a typical NEMA application, if they have been selected correctly. We know they do not protect under all running conditions, for example electronic and IEC versions include additional protection for single phase conditions.
I have never seen OL only functions properly protect large motors for conditions like, low voltage, single phasing, stalled/jam conditions, extended locked rotor during starting.