Locking Device

Status
Not open for further replies.

sii

Senior Member
Location
Nebraska
Anybody got a locking device for a CH120GF circuit breaker? My supply house couldn't come up with one. TIA
 
I have several types of breaker lock-outs but none of them will fit this breaker. I don't see anything on the Brady sight that looks like it would work either. Those Powerblocs look pretty handy but looks like they have to be purchased direct from the manufacturer?

View attachment 3981
 
What is the reason you need one of these? As Pierre mentioned there could be more than one required reason to use one. Depending on the reason, you may be limited as to the type of lockout device that you can actually use.
 
The circuit is the feed for a bandsaw that is hard-wired (as opposed to cord-and-plug connected) and I would like to be able to lock it out when working on it. Say no to stubs!
 
The circuit is the feed for a bandsaw that is hard-wired (as opposed to cord-and-plug connected) and I would like to be able to lock it out when working on it. Say no to stubs!


So you're looking for a required Article 422 disconnecting means for the saw?
 
Status
Not open for further replies.