Customer has 230' between house and barn driveway. Also has at least a 500' driveway to the county road. Any advice on how to illuminate these ?
They don't seem to be worried with costs on this job. What's the max length low voltage landscape lights can go ? Thanks !
 
Unless they only want low voltage I would go with line voltage and led bulbs.
And I agree with pton on the vd formula
 
When I did street lighting , I had a spread sheet to calc the volt drop, the load decreased at each light, as did the wire size.
 
Start by thinking about#10 AWG. Also start with a voltage drop calculation.
Maybe another service/transformer for the driveway lighting. Long term, it would be better.
 
Reading it again.

Those are long lengths for residence wiring. Think outside of the box.
 