 - Massachusetts
Gmack said:Why would you "stick" a box in limbo /between surfaces.
It does not matter why.
It only matters as far as this thread goes that it is not prohibited.
If one knows the thickness of a cabinet back, and the size of any space behind it, one can mount a nail-on (or box w/ring) that will end up flush with a cabinet interior.sandsnow said:It is stupid to intentionally make a box stick out beyond finish surface, especially where visible.
	infinity said:Around here receptacles mounted within cabinets always get a surface mounted wiremold box. We simply leave the cable sticking out of the wall and the cabinet guys cut out a hole leaving the cable in the cabinet. At the trim out a surface mounted box, receptacle and cover plate are installed. Done. No height problems or holes being cut too big or too small in the cabinet. Eliminates a lot of potential problems, especially the one that George mentioned.
Yes, the ones I use are. The part numbers are at this link.sandsnow said:Wait, are faceplates listed??? Hmmmm, I gotta check that.
.................................FIELD MODIFICATIONS
The UL Mark applies to the product as it is originally manufactured when shipped from the factory. Authorized use of the UL Mark is the manufacturer's declaration that the product was originally manufactured in accordance with the applicable requirements. UL does not know what the effect of a modification may have on the safety of the product or the continued validity of the UL certification mark unless the field modifications have been specifically investigated by UL. Unless UL investigates a modified product, UL cannot indicate that the product continues to meet UL's safety requirements.
The only exception for a field modification authorized by UL is when the product has specific replacement markings. For example, a switchboard may have specific grounding kits added in the field. The switchboard is marked with a list of specific kit numbers that have been investigated for use in that particular switchboard. Only grounding kits that are included on the product have been investigated for use in that product.
Do they use expanding spray foam insulation around boxes up there, Jeff? The only way I could use them is if they were set to 5/8" thickness, and then shifted them out at the trim - I wouldn't be able to wind them back in at the trim, because there would be expanda-foam behind them.jeff43222 said:One way I deal with the drywall guys burying my boxes is to use the adjustable ones Carlon makes.
Maybe, that's why I haven't decided yet.sandsnow said:Maybe I'm being too generous.??? Maybe I'm being too picky???
iwire said:Gmack said:Why would you "stick" a box in limbo /between surfaces.
I think you may be misunderstanding or taking it out of context.Mike Holt is quoted in several articles as saying that a box or extender must be flush.
	A box or extender "projecting" from a combustible surface would
violate code for "obvious" possible ignition reasons, more so if there were draft gaps around the cut opening.
"projecting therefrom" beyond the combustible surface is not the intention of 314 and to "reverse" and describe it as permissable is /was premature and not supportable.
cowboyjwc said:Things that I may have let go now go down on paper.
Please explain this. If you don't write it, you don't call it???? :?
You should also be there for your inspections as is required by law here in CA, ......
That is not required as far as I know. Please quote where this comes from. All that is required is permit card, approved plans, and work to be left uncovered for inspection.
Of course it is advantageous for the EC to be there.
cowboyjwc said:You're short an outlet in the bedroom at rough. Not going to write it down because it's going to be there at final. You trimmed an outlet plate, it's the only correction, do I really want to have to drive all the way back out there for that? You've done both things at the same inspection, down on paper they go and like I said since I'm writting I might as well get my inks worth. You get the idea.
OK, it still a correction.
Section 305.3 of the UAC "...It shall be the duty of the person requestiong any inspections required, either by thei Code or the Technical Codes, to provide access to and means for inspection of the work." Though the section may have changed, that's the one I have written down.
So, they don't have to be there. Leave ladders all over, covers off etc. We went through this and concluded no one has to be there.
Sorry I said state law. It's hard for them to provide access and means for inspection (ladders, tools, etc.) if they are not there also nothing worse than hearing "I don't know" over and over from whomever the EC left to walk with the inspector. Also it makes it easier for them to fix any simple corrections they may have and save us both a trip back.
True enough and convenient for both parties, but not a reason in itself to turn someone down.
My pride was hurt when he cited 110.12. I felt that was a cheap shot. I've seen much worse things pass (rough or trim). So, yes, on the second tag I was taken aback by that.cowboyjwc said:This isn't so much about what the corrections were as I think you are upset that "you have never been called on this before" and your pride is hurt because you got a correction notice.
I just don't have time for it. I seldom even know an inspection's in progress. Generally, there are fifteen other people with violations, and I'm a footnote on the list (if there at all.) This is the first time I've ever been the guy without a chair when the music stops - the only violations in the house were mine.You should also be there for your inspections..., that way you will better understand what he wants and not fix what you think he wants.
I don't understand this part. Can you elaborate?Now in his defense. I saw a code section...change...
Yes. I thought he was an electrician before, but I'm not sure.My final guess is that he is a combo inspector. Right?
I think you're saying that since you're walking with the electrician at the rough, and he's saying he'll install it when you leave, you're signing off and shaking hands. Very cool of you. 8)cowboyjwc said:You're short an outlet in the bedroom at rough. Not going to write it down because it's going to be there at final.
Generally, if there's a problem, then the super's on the phone and I'm there in about a minute. The super is big on talking to get the inspector to visit instead of inspect. I want no part of it. I have work to do, so does the inspector. If he finds something, fine: write it up. If it's a quick fix I can do it on the spot.As a coutresy to the inspector don't you think that it's a complete waste of his time to walk around with the Asst. Super. on a houseing tract and try to explain to him what the electrician needs to fix?
I truly appreciate it. I wanted to hear from everybody, otherwise I'd be telling my dog.Been in the trades almost 30 years and been a Chief Electrical Inspector or 17 of those. Just trying to pass on my experiance.