Re: Long Simmering Box Fill Question - Opinions wanted?
When a device box for a receptacle is roughed in with two many wires the inspector will turn it down on rough not wait until the receptacle is installed. Do we expect the inspector to make notes of every box in a house?
In the area that I live in the inspector will turn them down even if there was no wire in them. Should you want to use a 3 ? inch pancake box you best be mounting a door chime.
314.16 (A)
(A) Box Volume Calculations. The volume of a wiring enclosure (box) shall be the total volume of the assembled sections and, where used, the space provided by plaster rings, domed covers, extension rings, and so forth, that are marked with their volume or are made from boxes the dimensions of which are listed in Table 314.16(A).
I have always thought that the canopy is part of the light fixture and plays no role with the box.
The canopy is designed for the joints that the fixture will contain at the box.

When a device box for a receptacle is roughed in with two many wires the inspector will turn it down on rough not wait until the receptacle is installed. Do we expect the inspector to make notes of every box in a house?
In the area that I live in the inspector will turn them down even if there was no wire in them. Should you want to use a 3 ? inch pancake box you best be mounting a door chime.
314.16 (A)
(A) Box Volume Calculations. The volume of a wiring enclosure (box) shall be the total volume of the assembled sections and, where used, the space provided by plaster rings, domed covers, extension rings, and so forth, that are marked with their volume or are made from boxes the dimensions of which are listed in Table 314.16(A).
I have always thought that the canopy is part of the light fixture and plays no role with the box.
The canopy is designed for the joints that the fixture will contain at the box.