Looking through a drawing package i see reference for conduit sweep 'ells'. Is 'ells' an acronym, short for something or just a trade name for a special type of sweep? Trying to learn the lingo.
Building it as designed & as specified is one reason that comes to mind.... there is no real reason to use long radius bends.
Unless you have a long pull and need to reduce the sidewall pressure when the conductors are being installed, there is no real reason to use long radius bends.
The distinction is not between sweep ells and regular sweeps in terms of radius of curvature, it is between, for example, 45 degree sweeps and 90 degree sweeps.
Digger, what does this mean?
"Ell" is actually mostly a plumbing term for elbows. The utility industry, at least in my experience, calls a normal bend a 90 and a long bend a sweep. We require sweeps for all underground service conduits to reduce the pulling tension for service conductors. Easier for us to have a generic requirement than to specify the bends on every individual job. We also don't allow any "heated" bends because it can reduce the diameter of the conduit. Also a total of 180 deg. in the run. If it's a service conduit, submitting it to the utility can save a lot of extra work and expense.
Do they heat regular conduit to make factory PVC elbows? I have occasionally seen some of those that have questionable diameter or even out of round at the ends.We also don't allow any "heated" bends because it can reduce the diameter of the conduit.
I have bent a lot of small conduit without much trouble, 2, 2.5 and 3 inch I have made longer radius elbows with little problem, shorter radius bends are often difficult to make "bare handed" without distortion of the diameter of the pipe.I don't know how they mold PVC bends, but I'm guessing they use a mandrel with some sort of insert to maintain the inner diameter. I don't recall any that were out of round enough that they were difficult to fit to the next pipe section. Most of ours were already installed by the contractor. We just made 'em replace the sections that didn't meet our requirements. More than one UNhappy builder......but, hey, our requirements and our phone number were available on the internet, so not much sympathy. We have an electric conduit heater we use for our water pump station conduits, but we don't ever use 'em for services. I don't think it would be possible to make a "factory looking" bend with just a heater and bare hands. The stuff is really easy to kink. Again, it's just easier for us to make generic rules than to deal with every contractor's idea of what is OK. We're the ones who have to pull the cables, so we tend to be pretty strict. Time is money!![]()
"Ell" is actually mostly a plumbing term for elbows. The utility industry, at least in my experience, calls a normal bend a 90 and a long bend a sweep. We require sweeps for all underground service conduits to reduce the pulling tension for service conductors. Easier for us to have a generic requirement than to specify the bends on every individual job. We also don't allow any "heated" bends because it can reduce the diameter of the conduit. Also a total of 180 deg. in the run. If it's a service conduit, submitting it to the utility can save a lot of extra work and expense.
Do long radius sweeps really reduce pulling tension compared to their standard radius counterparts?
According to most pulling tension calculators, radius of sweep has zero effect on pulling tension. It affects side wall pressure, i.e. how localized the pulling tension and friction is on each fiber of raceway and insulation material, but not the net effect of pulling tension.
Not sure why the term was placed on the drawing with no spec as to a radius.
Good question, but I have to believe it does. Perhaps these "calculators" are giving you worst case?
With 48 inch radius I would guess.ell is slang or short for elbow. It can be ANY degrees. And any material. Typical plumbing talk. They also use the term bends and fraction of 360 degrees. i.e. a 90 degree elbow is a 1/4 bend.
Graybar use the term ELL for their electrical PVC elbow part numbers. i.e. ELL-45-6-48R. That is a 45 degree 6 inch elbow.
Do long radius sweeps really reduce pulling tension compared to their standard radius counterparts?
According to most pulling tension calculators, radius of sweep has zero effect on pulling tension. It affects side wall pressure, i.e. how localized the pulling tension and friction is on each fiber of raceway and insulation material, but not the net effect of pulling tension.