LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
Is there a post or thread that outlines pool-bonding requirements? I did a search and found too many threads to look through.
Found him, thank you!Search Kieth Lofland pool bonding, IMO he explains and shows it better than anyone.
Sorry Larry, how embarrassing.Found him, thank you!
(once I spelled Keith correctly )
I've done several pools and can offer what I've encountered. For the inground pools, I have done metal, partially recessed, fiberglass, and concrete, both poured and gunite. I'll start with the poured concrete pool.I feel like if I wait for the pool to be installed, these questions will answer themselves, but I'm being asked for a proposal now. The power circuitry I understand, just like any other equipment. The bonding wire need not even land in the panel.
I'll be running a feeder to an exterior panel on the back of the garage, where I'll supply the heat pump, the pump/controller, and a service receptacle. Must the feeder's EGC be insulated (PVC conduit), or must each branch circuit's EGC be?
There is a 3/4" PVC conduit feeding a mini-split for the garage. What I would like to do is re-use the conduit for a 60-amp feeder. May the mini-split be supplied by the same panel as the pool equipment, or must I run a separate feeder?
With #6 copper wire (largest in 3/4" PVC), may I use a 70a breaker, as long as the calculated load is no more than 65? I don't recall seeing a 65a breaker. How do motor/HVAC allowances affect feeder-breaker allowances? May I go larger?
Any and all suggestions and corrections are welcome. I hope to complete and send the proposal tonight.
Yes.With #6 copper wire (largest in 3/4" PVC), may I use a 70a breaker, as long as the calculated load is no more than 65?
Pretty sure you can go larger, but the governing code section for a feeder is 430.63, which I find confusing as it doesn't specify a maximum size, only a minimum size. I started a thread on this question but it hasn't yielded much clarity:I don't recall seeing a 65a breaker. How do motor/HVAC allowances affect feeder-breaker allowances? May I go larger?
As long as the mesh is a conductive material and at the correct distance from the pool walls it will suffice. If the mesh is used it would be fine to connect to it but might be easier to just split bolt it from one of the jumpers. You probably need to find out if the mesh used will be conductive so you know whether to use the bare #8 bonding ring as it would need to be placed and inspected before the pour. As well as the mesh, if used, would have to be inspected before the pour.Thank you, Bill. I was just told that it will be an in-ground pool with an aluminum wall shell, and there will be a poured-concrete surround. Will the reinforcing mesh the contractor uses also be adequate for the bonding?
I think four individual jumpers between the pool and the mesh sounds easiest. Where should I connect the bonding wire of the remote equipment, at the nearest point of the mesh, or should I take it to the pool shell?
Interesting read, thanx. That points directly to my situation. I have to supply the pool heat pump, the pump motor, and the existing garage mini-split. My main goal is to use the existing 3/4" PVC and avoid nuisance tripping of the feeder breaker.I started a thread on this question but it hasn't yielded much clarity:
Breezeway would be be enough here. They basically are looking for a roof connection. So, in your case no grounding electrode is needed.If I'm not mistaken, the breezeway defines the garage as attached in these-here parts.
The panel would end up on the outside of the garage, on the wall opposite the house.
Pool contractor should furnish the mesh, filter pump, & heat pump, or maybe the concrete contractor for the mesh. All I've ever furnished was the #8 and associated fittings. Split bolts are around $3 ea, lugs $5-$7 ea, not sure on the bare #8 but should be around .50 per ft. Also the contractor should furnish the ladder, handrails, mounting cups w/lugs etc.So, approximately how much does it cost for the necessary hardware? $100.00?
I have found a Greaves CBM310K CU Mesh Kit in the $700 range with shipping.
I'd need more clamps and jumpers, plus a length of #8 for the equipment run.