- New Jersey
- Journeyman Electrician (retired)
Why would we think that iwire would install 600' of EMT underground?
Why not use a vacuum and a mouse with a pull string attached? JMHO
I just think he didn't want to admit to two code violations in the same conduit run.
Say again. What violations?
Depending on what he is doing with the expansion fitting, there may be a 300.18 violation.
As long as he puts the joint back together while all he has in the pipe is his pull rope, he should be OK, yes?
Barring any issues with securing/supporting the joint....
You have a point there. It does say 'prior to the installation of conductors'.
He said split, he didn't say take apart.:happyno: Take apart, I don't have such a problem with. Split to me means something different for anyone who has had to repair a broken line and didn't want to pull the wire all the way out to repair it. I've heard.
Maybe I am overlooking something obvious, but why an expansion fitting as opposed to a C-condulet?
My guess would be buried.
If the condulet was not actually used as either a splice or a pull box, would Code still require it to be accessible (e.g. handhole)?
314.29 Boxes, Conduit Bodies, and Handhole Enclosures
to Be Accessible. Boxes, conduit bodies, and handhole
enclosures shall be installed so that the wiring contained
in them can be rendered accessible without removing
any part of the building or, in underground circuits, without
excavating sidewalks, paving, earth, or other substance that
is to be used to establish the finished grade.
Exception: Listed boxes and handhole enclosures shall be
permitted where covered by gravel, light aggregate, or noncohesive
granulated soil if their location is effectively identified
and accessible for excavation.
He said he used 2-200' fish tapes, he tied them together to have enough length.
Probably either because the thermal length change in the raceway over the temperature range required the expansion joint, or the expansion joint was installed at a structural expansion joint in the building.
In a run that long of EMT there is typically too much air loss from the fittings for a vacuum or blower to be effective.
I have never had that issue with compression couplings, but it is an issue with set screw couplings.In a run that long of EMT there is typically too much air loss from the fittings for a vacuum or blower to be effective.